Dutch of the Elm:
Have you checked IR readings L's-trunking, and N-trunking? I'd assume that normal IR testing would show up any inter-cable faults but it might be worth to check each line to trunking.
If trying to find an arcing fault, it might be best to use a test voltage of 500V or more, as opposed to 250V. Subject to disconnection of the load etc.
IR was with CPC connected to system earth (and so including trunking), 500v, so it would seem that the cable run itself is clear (all off the scale at >299Mohm)
Dutch of the Elm:
Have you checked IR readings L's-trunking, and N-trunking? I'd assume that normal IR testing would show up any inter-cable faults but it might be worth to check each line to trunking.
If trying to find an arcing fault, it might be best to use a test voltage of 500V or more, as opposed to 250V. Subject to disconnection of the load etc.
IR was with CPC connected to system earth (and so including trunking), 500v, so it would seem that the cable run itself is clear (all off the scale at >299Mohm)