ebee:
So if we have a number of lamposts in a field we could have :-
1/ Each lampost is it`s own TT electrode or
2/ As in 1/ above but all linked (from 1st to last) by a common cpc.
I`d instantly envisage the benefits of 2/ being a lower ohmic connection to "true earth" but what are the de-merits?
As I see it the problem is that the ground in different areas can be a significantly different potentials (especially during a HV fault) - near to the Tx (and so near the HV electrode) it might be thousands of volts above normal, a few metres away it might only be a few hundred, a few tens of metres it'll likely be more pretty much zero. Stood at any one point the voltage difference should be small (foot to foot or foot to hand on something metallic stuck into the ground right next to where you're standing) - but anything metallic spanning across those different areas risks exposing someone to a very large difference in voltage.
Hence the suggestion for a separate little TT island for each item.
I suppose another approach in theory would be a Class II approach - so no exposed-conductive-parts and the metallic column etc not bonded (but could be in contact with the soil) - but the UK's phobia about relying on double/reinforced insulation (e.g. 412.1.2) makes that approach tricky, especially for domestics.
- Andy.
ebee:
So if we have a number of lamposts in a field we could have :-
1/ Each lampost is it`s own TT electrode or
2/ As in 1/ above but all linked (from 1st to last) by a common cpc.
I`d instantly envisage the benefits of 2/ being a lower ohmic connection to "true earth" but what are the de-merits?
As I see it the problem is that the ground in different areas can be a significantly different potentials (especially during a HV fault) - near to the Tx (and so near the HV electrode) it might be thousands of volts above normal, a few metres away it might only be a few hundred, a few tens of metres it'll likely be more pretty much zero. Stood at any one point the voltage difference should be small (foot to foot or foot to hand on something metallic stuck into the ground right next to where you're standing) - but anything metallic spanning across those different areas risks exposing someone to a very large difference in voltage.
Hence the suggestion for a separate little TT island for each item.
I suppose another approach in theory would be a Class II approach - so no exposed-conductive-parts and the metallic column etc not bonded (but could be in contact with the soil) - but the UK's phobia about relying on double/reinforced insulation (e.g. 412.1.2) makes that approach tricky, especially for domestics.
- Andy.