Caravan RCD trip power connections

Dear all , a holiday question


I have an acquaintance who asks why his IET 18th Edition RCD tester when plugs it in to the Local RCD (<30mA/300mS) , the primary supply RCD trips (that is further up the AC supply line) , rather than the caravan’s, so in effect nullifying the test.

Is this because the Primary Supply RCD  is monitoring a small standing current from other connections and the Local RCD needs to be tested by using the Local Earth at the unit ? ( which is not so easily accessible). 


Are there any other thoughts please ? 


Paul , Swindon LN IET. 



Parents
  • If you have two non delayed RCDs cascading it could be one or the other or both that trip


    If one is delayed then it should trip last or not all , however you really need to densitive by a factor of three to be sure i;e:-

    10mA standard & 30mA delayed.

    30mA standard and 100mA delayed.

    for example


    If you test the upstream one on its own and get readings then there is a little trick you can do to bypass it to test the downstream one. But you need to know what you are doing otherwise potentially dangerous

Reply
  • If you have two non delayed RCDs cascading it could be one or the other or both that trip


    If one is delayed then it should trip last or not all , however you really need to densitive by a factor of three to be sure i;e:-

    10mA standard & 30mA delayed.

    30mA standard and 100mA delayed.

    for example


    If you test the upstream one on its own and get readings then there is a little trick you can do to bypass it to test the downstream one. But you need to know what you are doing otherwise potentially dangerous