Hello, not used this forum in a while and have had to re-register. I hope someone can help. I have an upcoming job to replace an existing small consumer unit in a garage about 30m from the house. The supply at the house is PME, and the current set up is a 4mm SWA fed from an MCB in the house CU, I recommended a switch fuse but the customer does not want this as it means destroying the wooden cabinet the existing CU is in. So the feed to the garage will be from a 32A mcb..Ive specified an earth rod at the garage as its concrete floor.is damp and dont want to export the PME. I will earth the outer armoured wire via the gland at the house end only, not at the garage end, and provide a TT earth system to the new garage CU.
My question is regarding rcd's ? The 2 way garage CU will have x2 30mA rcbo's for the outgoing circuits so then is there really a need for a 100ma main switch ? as it would serve no purpose. So to reiterate, the supply is SWA, protected by mcb at the house..If I use a 63A/100A mainswitch at the garage CU, will this be okay as it provides manual dp isolation., I want to reuse to existing garage CU and its metal.
The last time I installed an earth rod was over 20 years ago so want to