TT system for garage, RCD question

Hello, not used this forum in a while and have had to re-register. I hope someone can help. I have an upcoming job to replace an existing small consumer unit in a garage about 30m from the house. The supply at  the house is PME, and the current set up is a 4mm SWA fed from an MCB in the house CU,  I recommended a switch fuse but the customer does not want this as it means destroying the wooden cabinet the existing CU is in. So the feed to the garage will be from a 32A mcb..Ive specified an earth rod at the garage as its concrete floor.is damp and dont want to export the PME. I will earth the outer armoured wire via the gland at the house end only, not at the garage end, and provide a TT earth system to the new garage CU.


My question is regarding rcd's ? The 2 way garage CU will have x2 30mA  rcbo's for the outgoing circuits so then is there really a need for a 100ma main switch ? as it would serve no purpose. So to reiterate, the supply is SWA, protected by mcb at the house..If I use a 63A/100A mainswitch at the garage CU, will this be okay as it provides manual dp isolation., I want to reuse to existing garage CU and its metal.


The last time I installed an earth rod was over 20 years ago so want to
Parents
  • If you have an installation with TN-C-S PME earthing and you create a TT installation within it to supply a garage as a island, does the neutral of the supply cable from the house into the garage stop being part of the main house installation?

    I'm not sure, I'm correctly anticipating the question behind that, but ...


    The N would need to be treated as part of the TT system once you're in an environment where anyone working on it might be in contact with the TT system's PE conductors rather than the main installation's PE conductors. It's not so much the absolute voltage on the N that's the concern but the voltage difference between N and PE.


    An uncleared L-true Earth fault can result in the N floating a long way from true Earth - on a TN system PE will follow N, on TT it won't.


       - Andy.
Reply
  • If you have an installation with TN-C-S PME earthing and you create a TT installation within it to supply a garage as a island, does the neutral of the supply cable from the house into the garage stop being part of the main house installation?

    I'm not sure, I'm correctly anticipating the question behind that, but ...


    The N would need to be treated as part of the TT system once you're in an environment where anyone working on it might be in contact with the TT system's PE conductors rather than the main installation's PE conductors. It's not so much the absolute voltage on the N that's the concern but the voltage difference between N and PE.


    An uncleared L-true Earth fault can result in the N floating a long way from true Earth - on a TN system PE will follow N, on TT it won't.


       - Andy.