Dwallywombat:
Note that "high integrity" sockets are unrelated to a clean earth; the former are for where high cpc currents are expected and two cpcs may be needed [543.7.1.204].
Shoot me down if I have it wrong, if you have a second supplementary oversized CPC any voltage difference that may be present across the earth terminals of adjacent sockets supplying two items of audio equipment due to earth leakage from the equipment will be significantly reduced, which will reduce any current that may follow along the cable screens of audio cables linking them, which will reduce the interference.
Andy Betteridge
Dwallywombat:
Note that "high integrity" sockets are unrelated to a clean earth; the former are for where high cpc currents are expected and two cpcs may be needed [543.7.1.204].
Shoot me down if I have it wrong, if you have a second supplementary oversized CPC any voltage difference that may be present across the earth terminals of adjacent sockets supplying two items of audio equipment due to earth leakage from the equipment will be significantly reduced, which will reduce any current that may follow along the cable screens of audio cables linking them, which will reduce the interference.
Andy Betteridge