Chris Pearson:
I have to say that I find it doubtful that the ordinary human ear can perceive this apparent "noise'. What is the evidence that it can?
A 50Hz hum is within a lot of people’s hearing range as most of us can hear right down to 20Hz or so, the evidence...just ask any stage leckie or techie There’s only about a million of us in this country. We all know about low hums and earth loop noises (not the same as earth fault loop).
IronFreely:
I’m just wondering about how clean earth sockets (Some of you may call these high integrity sockets) fit into the requirements of BS7671 in terms of their use in domestic homes.
One of my clients has asked me to look into the use of some clean earth sockets to be used to power audio equipment in their home studio, the basic idea is that a completely separate Earth helps eliminate what’s known as an earth hum on audio equipment caused by functional earth leakage of other equipment connected to the same circuit and disturbances originating from the suppliers earthing arrangement. The basic concept seems to be to insulate the cpc from the earth terminal of the socket outlet which then has its own independent Earth electrode, high integrity sockets seem designed to accept and insulate a cpc and a separate earth.
My concern is that this sort of thing is usually used in a restricted access environment where only IT or audio engineers are going to be around and might be considered trained and competent to understand the risk of introducing an earth potential to the equipotential zone that is not in itself connected to the equipotential bonding. It wouldn’t be a problem if I could guarantee restricted access or that the socket would only supply class 2 equipment, but as this is a home studio it seems a bad idea to have an earthed metal casing of some piece of audio equipment that may be completely separate from all other earthing and bonding in the property?
id appreciate your thoughts and advice please, I’m confident a separate clean earth will resolve the earth hum problem which I’ve seen work well in theatres (essentially restricted access) before but never in a domestic property.
Edit: I should add that the property is a TT property but because the street is a hodgepodge of TNS and TNCS (I have other neighbouring clients really close by) you should assume the gas and water pipe are throwing in a bit of PME related disturbance.
Dwallywombat:
Note that "high integrity" sockets are unrelated to a clean earth; the former are for where high cpc currents are expected and two cpcs may be needed [543.7.1.204].
Shoot me down if I have it wrong, if you have a second supplementary oversized CPC any voltage difference that may be present across the earth terminals of adjacent sockets supplying two items of audio equipment due to earth leakage from the equipment will be significantly reduced, which will reduce any current that may follow along the cable screens of audio cables linking them, which will reduce the interference.
Andy Betteridge
Sparkingchip:Dwallywombat:
Note that "high integrity" sockets are unrelated to a clean earth; the former are for where high cpc currents are expected and two cpcs may be needed [543.7.1.204].Shoot me down if I have it wrong, if you have a second supplementary oversized CPC any voltage difference that may be present across the earth terminals of adjacent sockets supplying two items of audio equipment due to earth leakage from the equipment will be significantly reduced, which will reduce any current that may follow along the cable screens of audio cables linking them, which will reduce the interference.
Andy Betteridge
You'd need to be talking some amount of "oversizing" to achieve this, perhaps above the csa that's allowed for in a BS 1363-2 socket-outlet - multiple functional bonds to a local earth bar are far more efective, as are so-called "cross-bonds". This is why rack mounted PDUs often have a separate external M4, M6 or M8 earth stud.
IronFreely:Chris Pearson:
I have to say that I find it doubtful that the ordinary human ear can perceive this apparent "noise'. What is the evidence that it can?A 50Hz hum is within a lot of people’s hearing range as most of us can hear right down to 20Hz or so, the evidence...just ask any stage leckie or techie There’s only about a million of us in this country. We all know about low hums and earth loop noises (not the same as earth fault loop).
I know fine well what mains hum is. So what is the amplitude of the one that you are seeking to abolish?