RCDs on 110v sockets

Do 110v sockets require rcd protection?
Parents
  • To be clear, RCD protection is not required by 7671 for socket outlets on reduced low voltage systems such as are commonly found on construction sites in the U.K.
Reply
  • To be clear, RCD protection is not required by 7671 for socket outlets on reduced low voltage systems such as are commonly found on construction sites in the U.K.