Do 110v sockets require rcd protection?
Parents
  • To be clear, RCD protection is not required by 7671 for socket outlets on reduced low voltage systems such as are commonly found on construction sites in the U.K.

    Agreed - now I look carefully it's spelled out clearly in the last paragraph of 411.3.3 itself (promoted from just a NOTE in the 17th) - "The requirements of Regulation 411.3.3 do not apply to FELV systems according to Regulation 411.7 or reduced low voltage systems according to Regulation 411.8".

        - Andy.
Reply
  • To be clear, RCD protection is not required by 7671 for socket outlets on reduced low voltage systems such as are commonly found on construction sites in the U.K.

    Agreed - now I look carefully it's spelled out clearly in the last paragraph of 411.3.3 itself (promoted from just a NOTE in the 17th) - "The requirements of Regulation 411.3.3 do not apply to FELV systems according to Regulation 411.7 or reduced low voltage systems according to Regulation 411.8".