Is it necessary to bond both sides of an armoured cable if it’s not being used as a CPC and if you bond it at the supply side of an electrical motor starter panel is there anything in the regs where it should be bonded too or can it just be bolted to the chassis stud using a 6mm fly lead off the gland. 


thanks for your help in advance guys.
Parents
  • are you relying on the earthed armour to avoid having to have an RCD at the origin, and or conduit or a visible route?


    If so it should be earthed at the supply end.  It need not be bonded at the load end, but unless you are creating a TT island you normally would connect to the CPC at both ends, it just lowers the effective CPC resistance a bit, and it is also good practice from an EMC point of view.

    Regs do not oblige you to earth at one end or the other or indeed in the middle, but requiring ADS to work normally means you do.
Reply
  • are you relying on the earthed armour to avoid having to have an RCD at the origin, and or conduit or a visible route?


    If so it should be earthed at the supply end.  It need not be bonded at the load end, but unless you are creating a TT island you normally would connect to the CPC at both ends, it just lowers the effective CPC resistance a bit, and it is also good practice from an EMC point of view.

    Regs do not oblige you to earth at one end or the other or indeed in the middle, but requiring ADS to work normally means you do.