The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement

This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Bonding both sides of an swa cable

Is it necessary to bond both sides of an armoured cable if it’s not being used as a CPC and if you bond it at the supply side of an electrical motor starter panel is there anything in the regs where it should be bonded too or can it just be bolted to the chassis stud using a 6mm fly lead off the gland. 


thanks for your help in advance guys.
Parents
  • So if the gland plate is bonded to the chassis of the MCC would you again run a separate flylead to the earth bar.
Reply
  • So if the gland plate is bonded to the chassis of the MCC would you again run a separate flylead to the earth bar.
Children
No Data