Bonding both sides of an swa cable

Is it necessary to bond both sides of an armoured cable if it’s not being used as a CPC and if you bond it at the supply side of an electrical motor starter panel is there anything in the regs where it should be bonded too or can it just be bolted to the chassis stud using a 6mm fly lead off the gland. 


thanks for your help in advance guys.
Parents
  • MrJack96:

    Thanks guys. So there is a requirement on sizing the earth links to the required size to carry fault current. As I’ve only really seen armoured coming into the gland plate and it’s mostly always daisy chained with 6mm2 cable. I don’t know if there’s any tables I can use. Thanks again guys. 


    Odd terminology again ("earth links") but see 543.1.1


Reply
  • MrJack96:

    Thanks guys. So there is a requirement on sizing the earth links to the required size to carry fault current. As I’ve only really seen armoured coming into the gland plate and it’s mostly always daisy chained with 6mm2 cable. I don’t know if there’s any tables I can use. Thanks again guys. 


    Odd terminology again ("earth links") but see 543.1.1