The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement

This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Bonding both sides of an swa cable

Is it necessary to bond both sides of an armoured cable if it’s not being used as a CPC and if you bond it at the supply side of an electrical motor starter panel is there anything in the regs where it should be bonded too or can it just be bolted to the chassis stud using a 6mm fly lead off the gland. 


thanks for your help in advance guys.
Parents
  • What is the requirements when your feeding from a MCC through JBs to a local isolator.(if it’s been earthed at the MCC) I see continuity kept by linking all the armours together (daisy chaining) usually in the junction boxes or isolators but not sure what good practice should be used.
Reply
  • What is the requirements when your feeding from a MCC through JBs to a local isolator.(if it’s been earthed at the MCC) I see continuity kept by linking all the armours together (daisy chaining) usually in the junction boxes or isolators but not sure what good practice should be used.
Children
No Data