pat testing questions

Former Community Member
Former Community Member
Today I failed my pat testing exam. I was presented with questions not covered by the tutor during the course and cannot find clarification in the iet book I was hoping to get some answers.


A few of the questions where about rcd sockets outdoors, the maximum trip time and trip values as well as minimum and maximum amperage.


Another 2 was about test probe leads, the question answers had options like bs codes and gs38 and also voltage ratings like 20-200v ac and 20-200v dc. But none of this was covered in the course.


I failed by a single mark. Had these been covered or easy to find in the book I would have passed. Can anyone offer clarification in relation to this information?
Parents
  • Bad luck on the test, but perhaps better to understand it fully before being released into the wild!  I have no idea what is in your PAT syllabus, so cannot comment on if the tutor was directing you to the right info or not,  but I'll have a go at the queries. Easy one first

    gs38 - guidance for probe tips on meters and when you need precautions like fused test leads,


    How good is your understanding of how things like RCDs and fuses work ?  If the below makes no sense, then some more background reading is needed, so if need bo feel free to come back and I can point you to that.

    question about current rating of what ? do you know how to select the right  fuse  for a plug or fused spur? Was this about test kit with larger sockets? -the needs for  63A 3 phase plugs are a bit different to those for shavers..


    RCDs that are intended to save lives, as opposed to save wiring from damage, have to remove the power in less than a heartbeat - typically 0.4 of a second for systems like 230V mains on TN supplies, where a max shock voltage of 115 is assumed. ).2 seconds in situations with a high impedance earth where the shock voltage may be the full supply voltage. Actually in a modern installation nearly all 13A sockets are fed by an RCD of sime kind, but the high risks are hand held things, and stuff used where it may be wet, like outdoor, or bathrooms/ swimming pools etc.

Reply
  • Bad luck on the test, but perhaps better to understand it fully before being released into the wild!  I have no idea what is in your PAT syllabus, so cannot comment on if the tutor was directing you to the right info or not,  but I'll have a go at the queries. Easy one first

    gs38 - guidance for probe tips on meters and when you need precautions like fused test leads,


    How good is your understanding of how things like RCDs and fuses work ?  If the below makes no sense, then some more background reading is needed, so if need bo feel free to come back and I can point you to that.

    question about current rating of what ? do you know how to select the right  fuse  for a plug or fused spur? Was this about test kit with larger sockets? -the needs for  63A 3 phase plugs are a bit different to those for shavers..


    RCDs that are intended to save lives, as opposed to save wiring from damage, have to remove the power in less than a heartbeat - typically 0.4 of a second for systems like 230V mains on TN supplies, where a max shock voltage of 115 is assumed. ).2 seconds in situations with a high impedance earth where the shock voltage may be the full supply voltage. Actually in a modern installation nearly all 13A sockets are fed by an RCD of sime kind, but the high risks are hand held things, and stuff used where it may be wet, like outdoor, or bathrooms/ swimming pools etc.