The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement

This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

elcb and borehole pump

Former Community Member
Former Community Member
Hello

I have a problem with a newly installed domestic borehole pump. This is to replace the original pump which after 20 years has given up the ghost.

The pump appears to operate satisfactorily except that it trips the consumer unit elcb on starting and only on starting. Resetting the elcb allows the pump to run normally. The time taken to push the elcb switch back up is presumably sufficient for some transient effect to end.


The house wiring is exactly the same as for the original pump, which ran satisfactorily for 20 years.


The installer has carried out all the tests normally conducted on the pump and pump cable (continuity, insulation, running current, etc.) and claims that the pump is not faulty. Yet it trips the elcb on startup.


I will welcome any suggestions for a solution. The installer is a one man firm and is reluctant (to say the least) to change the pump.


Mike Lee
Parents
  • Former Community Member
    0 Former Community Member
    Andy

    I use CEF because they have a depot within a couple of miles of us. Their web site is a bit confusing, but I did find a full range of RCDs. Thanks for the tip about type A.


    The borehole top-casing is plastic, so nothing to connect an earth to.
Reply
  • Former Community Member
    0 Former Community Member
    Andy

    I use CEF because they have a depot within a couple of miles of us. Their web site is a bit confusing, but I did find a full range of RCDs. Thanks for the tip about type A.


    The borehole top-casing is plastic, so nothing to connect an earth to.
Children
No Data