Zs, to test or calculate?

A large contractor working on our site have told me yesterday that it is their policy not to live test final circuits where they cannot use a plug? In order to reduce risk, they will now only calculate Zs, on circuits where they would have to open an enclosure, such as FCU's and light fittings.
The control measures we insist are in place, are IP2X equipment, GS38 leads, two man rule with second man having resus training, among others. So I feel the risk has been reduced to as low as reasonably practicable. An d my instinct tells me that a measured Zs reading must be more accurate than a calculated one, since it will include all parallel paths under test.
The contractor is happy to live test distribution circuits, so it seems they want to pick and choose.
They also state that this is how things are now, and have worked at many different sites, Cross Rail, Heathrow, various MOD sites etc, and that they al accept this as common practice.

I like some opinions to find out what's going on out there on other sites. 
Parents
  • I agree with the risk reduction measures, particularly where there is an alternative "dead test" method.


    That is common-sense application of the hierarchy of control - "remove the hazard" being the first option in all cases.


    To continue to conduct live tests where an alternative method is available - using figures you may already have from previous dead tests, say if you adopt (R1+R2) for a combined earth continuity and polarity test - leaves you wide open to greater scrutiny in the event someone gets hurt.


    Because of this, I don't think there's an argument you could use that will convince the site management and their health & safety advisors, otherwise.
Reply
  • I agree with the risk reduction measures, particularly where there is an alternative "dead test" method.


    That is common-sense application of the hierarchy of control - "remove the hazard" being the first option in all cases.


    To continue to conduct live tests where an alternative method is available - using figures you may already have from previous dead tests, say if you adopt (R1+R2) for a combined earth continuity and polarity test - leaves you wide open to greater scrutiny in the event someone gets hurt.


    Because of this, I don't think there's an argument you could use that will convince the site management and their health & safety advisors, otherwise.