Zs, to test or calculate?

A large contractor working on our site have told me yesterday that it is their policy not to live test final circuits where they cannot use a plug? In order to reduce risk, they will now only calculate Zs, on circuits where they would have to open an enclosure, such as FCU's and light fittings.
The control measures we insist are in place, are IP2X equipment, GS38 leads, two man rule with second man having resus training, among others. So I feel the risk has been reduced to as low as reasonably practicable. An d my instinct tells me that a measured Zs reading must be more accurate than a calculated one, since it will include all parallel paths under test.
The contractor is happy to live test distribution circuits, so it seems they want to pick and choose.
They also state that this is how things are now, and have worked at many different sites, Cross Rail, Heathrow, various MOD sites etc, and that they al accept this as common practice.

I like some opinions to find out what's going on out there on other sites. 
Parents
  • In the back of my van I have a telescopic fibreglass R2 testing pole, I used it to test a light on the gable of a house a couple of weeks ago, I don't intend to take an extension ladder to check a light such as that for an EICR, visual and continuity testing with both feet on the ground.


    However when replacing a light fitting and access equipment is already in place then I would loop test, as these were site cabins being installed that were already being wired before delivery to site some testing is required, if need be I would test at a switch with two feet safely on the floor, but obviously that may require a two lead loop tester and I have a couple to use.


    There is a precedent.

    https://www.manchestereveningnews.co.uk/news/greater-manchester-news/dads-agony-after-apprentice-electrician-9085985


    Andy B.


Reply
  • In the back of my van I have a telescopic fibreglass R2 testing pole, I used it to test a light on the gable of a house a couple of weeks ago, I don't intend to take an extension ladder to check a light such as that for an EICR, visual and continuity testing with both feet on the ground.


    However when replacing a light fitting and access equipment is already in place then I would loop test, as these were site cabins being installed that were already being wired before delivery to site some testing is required, if need be I would test at a switch with two feet safely on the floor, but obviously that may require a two lead loop tester and I have a couple to use.


    There is a precedent.

    https://www.manchestereveningnews.co.uk/news/greater-manchester-news/dads-agony-after-apprentice-electrician-9085985


    Andy B.