Zs, to test or calculate?

A large contractor working on our site have told me yesterday that it is their policy not to live test final circuits where they cannot use a plug? In order to reduce risk, they will now only calculate Zs, on circuits where they would have to open an enclosure, such as FCU's and light fittings.
The control measures we insist are in place, are IP2X equipment, GS38 leads, two man rule with second man having resus training, among others. So I feel the risk has been reduced to as low as reasonably practicable. An d my instinct tells me that a measured Zs reading must be more accurate than a calculated one, since it will include all parallel paths under test.
The contractor is happy to live test distribution circuits, so it seems they want to pick and choose.
They also state that this is how things are now, and have worked at many different sites, Cross Rail, Heathrow, various MOD sites etc, and that they al accept this as common practice.

I like some opinions to find out what's going on out there on other sites. 
Parents
  • davezawadi (David Stone):

    Well Graham, perhaps you have hit the nail on the head. I like to do testing with 2 people with radio communications, it is very much quicker, and overcomes your idea that an open accessory or whatever left with a meter and perhaps a warning notice is dangerous to anyone. The idea that one man tests a large installation by walking miles each day is simply arcane.

    Hang on ... you mentioned the isolate ... connect ... renergize process?

    We are in the 21st-century and need to use 21st-century tools. R1 + R2 testing takes very little time, insulation testing has someone close to the items being tested etc. You can see how this is so much safer and quicker but want to give a method statement and procedure which removes the value of the work.

    Even with 2 people, it's still unfortunately a "process" or "method" vs "safety". As I said, it's not a matter of changing "what the electrician thinks is best" on these sites, but convincing the H&S Team - who might well be held at least partly to account if the maintenance checks on their electrical systems were deemed inadequate, so I guess after all it's their call.

    So be it, but I hope there is never a problem due to inadequate testing, it is likely one day. Personally I have no problem with live testing at all, but then I am of that age.

    So, you mentioned 21st century.


    I have a feeling that we are at a point where loop testing and prospective fault current testing might be a thing of the past ... because microgeneration with inverter output can provide a totally erroneous and meaningless reading.
Reply
  • davezawadi (David Stone):

    Well Graham, perhaps you have hit the nail on the head. I like to do testing with 2 people with radio communications, it is very much quicker, and overcomes your idea that an open accessory or whatever left with a meter and perhaps a warning notice is dangerous to anyone. The idea that one man tests a large installation by walking miles each day is simply arcane.

    Hang on ... you mentioned the isolate ... connect ... renergize process?

    We are in the 21st-century and need to use 21st-century tools. R1 + R2 testing takes very little time, insulation testing has someone close to the items being tested etc. You can see how this is so much safer and quicker but want to give a method statement and procedure which removes the value of the work.

    Even with 2 people, it's still unfortunately a "process" or "method" vs "safety". As I said, it's not a matter of changing "what the electrician thinks is best" on these sites, but convincing the H&S Team - who might well be held at least partly to account if the maintenance checks on their electrical systems were deemed inadequate, so I guess after all it's their call.

    So be it, but I hope there is never a problem due to inadequate testing, it is likely one day. Personally I have no problem with live testing at all, but then I am of that age.

    So, you mentioned 21st century.


    I have a feeling that we are at a point where loop testing and prospective fault current testing might be a thing of the past ... because microgeneration with inverter output can provide a totally erroneous and meaningless reading.