gkenyon:Sparkingchip:Is opening the ceiling rose of a pendant, which does not require any tools to test anymore dangerous than removing the cover of the consumer unit to test Ze, etc?
Andy B
Polarity Test can be a dead test, and in that respect is far less dangerous than removing the cover of the consumer unit to conduct live tests.
Connecting a loop tester performed more than one test at the same time.
To be honest when changing a light fitting I will connect the tester to check polarity, loop impedance and then trip the RCD if there is one before taking down the old fitting, then walked back to the consumer unit to isolate, then confirm the fitting is dead and so on and do forth. Bearing in mind there's lots shoddy wiring out there to catch out the unwary, like the Bulgarian builder who dismantled this socket fitting and the bathroom fitter who pulled the cable into the back of it.
gkenyon:Sparkingchip:Is opening the ceiling rose of a pendant, which does not require any tools to test anymore dangerous than removing the cover of the consumer unit to test Ze, etc?
Andy B
Polarity Test can be a dead test, and in that respect is far less dangerous than removing the cover of the consumer unit to conduct live tests.
Connecting a loop tester performed more than one test at the same time.
To be honest when changing a light fitting I will connect the tester to check polarity, loop impedance and then trip the RCD if there is one before taking down the old fitting, then walked back to the consumer unit to isolate, then confirm the fitting is dead and so on and do forth. Bearing in mind there's lots shoddy wiring out there to catch out the unwary, like the Bulgarian builder who dismantled this socket fitting and the bathroom fitter who pulled the cable into the back of it.