Zs, to test or calculate?

A large contractor working on our site have told me yesterday that it is their policy not to live test final circuits where they cannot use a plug? In order to reduce risk, they will now only calculate Zs, on circuits where they would have to open an enclosure, such as FCU's and light fittings.
The control measures we insist are in place, are IP2X equipment, GS38 leads, two man rule with second man having resus training, among others. So I feel the risk has been reduced to as low as reasonably practicable. An d my instinct tells me that a measured Zs reading must be more accurate than a calculated one, since it will include all parallel paths under test.
The contractor is happy to live test distribution circuits, so it seems they want to pick and choose.
They also state that this is how things are now, and have worked at many different sites, Cross Rail, Heathrow, various MOD sites etc, and that they al accept this as common practice.

I like some opinions to find out what's going on out there on other sites. 
Parents
  • Sparkingchip:

    Connecting a loop tester performed more than one test at the same time. 


    To be honest when changing a light fitting I will connect the tester to check polarity,  loop impedance and then trip the RCD if there is one before taking down the old fitting,  then walked back to the consumer unit to isolate,  then confirm the fitting is dead and so on and do forth. 




    Agreed ... but ... Polarity test should be conducted BEFORE energization, see Regulation 643.1



    And regards the other situation ... yes, I'm sure we get too many of those.


Reply
  • Sparkingchip:

    Connecting a loop tester performed more than one test at the same time. 


    To be honest when changing a light fitting I will connect the tester to check polarity,  loop impedance and then trip the RCD if there is one before taking down the old fitting,  then walked back to the consumer unit to isolate,  then confirm the fitting is dead and so on and do forth. 




    Agreed ... but ... Polarity test should be conducted BEFORE energization, see Regulation 643.1



    And regards the other situation ... yes, I'm sure we get too many of those.