Zs, to test or calculate?

A large contractor working on our site have told me yesterday that it is their policy not to live test final circuits where they cannot use a plug? In order to reduce risk, they will now only calculate Zs, on circuits where they would have to open an enclosure, such as FCU's and light fittings.
The control measures we insist are in place, are IP2X equipment, GS38 leads, two man rule with second man having resus training, among others. So I feel the risk has been reduced to as low as reasonably practicable. An d my instinct tells me that a measured Zs reading must be more accurate than a calculated one, since it will include all parallel paths under test.
The contractor is happy to live test distribution circuits, so it seems they want to pick and choose.
They also state that this is how things are now, and have worked at many different sites, Cross Rail, Heathrow, various MOD sites etc, and that they al accept this as common practice.

I like some opinions to find out what's going on out there on other sites. 
Parents
  • Sparkingchip:

    You have to do a live test somewhere along the line.


    Three phase you will be checking the phase sequence as well as polarity, I had an interesting discussion with two electricians in a pub one night, one of them works for a generator hire company and makes great use of a long wander lead to ensure he is hooking up temporary supplies correctly.


    Andy B.




    Agreed - but perhaps we need to consider whether it's a loop impedance test when we have lots of microgeneration sources out there. The results using current test methods could well be largely meaningless.


Reply
  • Sparkingchip:

    You have to do a live test somewhere along the line.


    Three phase you will be checking the phase sequence as well as polarity, I had an interesting discussion with two electricians in a pub one night, one of them works for a generator hire company and makes great use of a long wander lead to ensure he is hooking up temporary supplies correctly.


    Andy B.




    Agreed - but perhaps we need to consider whether it's a loop impedance test when we have lots of microgeneration sources out there. The results using current test methods could well be largely meaningless.