Shower 32amp breaker

Former Community Member
Former Community Member
I’ve now seen this a few times, an 8.5kw shower on 6mm t&e with a 32amp breaker.

My question is:

Why do electricians do this, and is it detrimental to the breaker?

Parents
  • Former Community Member
    0 Former Community Member
    So from the above help, it seems that this is not an uncommon occurrence. And not detrimental to the MCB

    To add more detail, the installation that I refer to is a replacement CU. previously the shower was on a  B40 MCB, cable method is 6mm t&e clipped direct with no insulation. Cable run is approximately 10m


    The shower is also using around 38A according to my clamp meter
Reply
  • Former Community Member
    0 Former Community Member
    So from the above help, it seems that this is not an uncommon occurrence. And not detrimental to the MCB

    To add more detail, the installation that I refer to is a replacement CU. previously the shower was on a  B40 MCB, cable method is 6mm t&e clipped direct with no insulation. Cable run is approximately 10m


    The shower is also using around 38A according to my clamp meter