Panel Isolators - Different Voltages?

Where different voltages are fed into a panel is it permitted to isolate them both through the same isolator?
  • For example where you have a Main Fused Isolator for an incoming 3ph supply and a 110Vdc incoming from a UPS?

  • My experience says that as you quite often get auxiliary isolation contacts then it is possible.

  • However should these auxiliary contacts only be used for signalling and therefore cannot be used as a mean of isolation?

  • Also I frequently see 3 or 4 pole isolator used for single phase supply so can you use the remaining contacts to isolate another voltage?


Any thoughts would be most welcome.
Parents
  • Agreed @broadgage - this is permitted in BS EN 60204-1, and a reason I also stated "many ELV supplies", not "all ELV supplies". BS EN 60204-1 requires different coloured conductor identification for circuits not under control of the panel isolator as another indication.


    I just thought it was worth highlighting that danger (and hence requirement for isolation) is not just an LV issue.
Reply
  • Agreed @broadgage - this is permitted in BS EN 60204-1, and a reason I also stated "many ELV supplies", not "all ELV supplies". BS EN 60204-1 requires different coloured conductor identification for circuits not under control of the panel isolator as another indication.


    I just thought it was worth highlighting that danger (and hence requirement for isolation) is not just an LV issue.