LED inrush current and generator set

Hello,


I'm currently working on a sport field application where i need to power some LED reflectors (30 kW total).

I will also use a generator set, in case the network fails.


The inrush current of the reflectors is 3 times higher than their rated current, but the duration is only 0.2ms.


Could anybody tell me if i should take into account the inrush current when I choose the generator set power (that is, to oversize the generator)?

Or i should ignore the inrush current and set the power of the generator a bit higher than the total power of the reflectors?

I'm not talking about the circuit breakers of generator's outputs. Let's say one can choose them so that they don't trip.

If those breakers don't trip, is it possible that anything else happen to the generator set, because of the inrush current?


I've been searching through the specifications of many generator sets, but i cannot find any data on this specific problem (short overload).






Parents
  • Since this is for a back-up supply for a sports field, I guess that the main need for lighting will be during a match etc.  Is it therefore worth hiring in a mobile generator, once the lights are in situ, to trial both a suitable staged switch on;  ie delays between banks being energised and the kVA rating of a suitable generator?
Reply
  • Since this is for a back-up supply for a sports field, I guess that the main need for lighting will be during a match etc.  Is it therefore worth hiring in a mobile generator, once the lights are in situ, to trial both a suitable staged switch on;  ie delays between banks being energised and the kVA rating of a suitable generator?