AJJewsbury:Also is there a single on/off switch that controls all 30 kW of lighting at once?
Indeed - simple sequential start arrangements (anything from a lot of carefully co-ordinated on-delay timers to just a bank of separate lightswitches) can side-step a lot of inrush problems.
- Andy.
This will be the final solution.
I was just trying to understand if the generator could be damaged from high currents of short duration.
AJJewsbury:Also is there a single on/off switch that controls all 30 kW of lighting at once?
Indeed - simple sequential start arrangements (anything from a lot of carefully co-ordinated on-delay timers to just a bank of separate lightswitches) can side-step a lot of inrush problems.
- Andy.
This will be the final solution.
I was just trying to understand if the generator could be damaged from high currents of short duration.