broadgage:
The inrush current drawn by LED lamps is extremely brief and unlikely to have significant effects on a generator.
I would however be inclined to oversize the generator on general principles, life and reliability will be enhanced by not running right at the limit.
Load tends to grow.
LED lights may have an odd waveform, also making oversizing prudent.
They don't say anything about the waveform or harmonics... They only specify the power factor, which is 0.95.
The theory says that a generator should ideally be loaded at 70...90% of its capacity.
Oversizing considering that those 30 kW represent 70...80% of the generator capacity is enough, in your opinion?
Considering that, in the future, only small changes in the load will be made...
broadgage:
The inrush current drawn by LED lamps is extremely brief and unlikely to have significant effects on a generator.
I would however be inclined to oversize the generator on general principles, life and reliability will be enhanced by not running right at the limit.
Load tends to grow.
LED lights may have an odd waveform, also making oversizing prudent.
They don't say anything about the waveform or harmonics... They only specify the power factor, which is 0.95.
The theory says that a generator should ideally be loaded at 70...90% of its capacity.
Oversizing considering that those 30 kW represent 70...80% of the generator capacity is enough, in your opinion?
Considering that, in the future, only small changes in the load will be made...