Harry Macdonald:
There are installations where a diesel generator assumes full load in 3 seconds from cold start but they are rather specialist and I don't know to what extent the generator was oversized to allow this.
I don't think it unreasonable to start the generator immediately but to let it run for 5 secs before initialing the change over to see if it is a real power cut. Then you hit the step load issue and need to keep the load steps below 1/4 of capacity per step so 5 steps changes in the next 5 seconds should be reasonable.
However this all needs careful control and you also need to think about how the transfer back to mains power is arranged. Automatic or manual? What happens if the power if restored while the loads are being switched on the the generator?
Sorry for the delayed answer.
Thank you for reminding me about these details.
I think that the simplest way is that the transfer back to mains to be made manually. I think some ATS have implemented this function - i found this text on a specification: "if the mains supply becomes available again before the generator circuit breaker has closed then the mains circuit breaker remains closed (or recloses if it has opened) and the generator will not go on load.".
Are all these details manageable by a PLC?
Harry Macdonald:
There are installations where a diesel generator assumes full load in 3 seconds from cold start but they are rather specialist and I don't know to what extent the generator was oversized to allow this.
I don't think it unreasonable to start the generator immediately but to let it run for 5 secs before initialing the change over to see if it is a real power cut. Then you hit the step load issue and need to keep the load steps below 1/4 of capacity per step so 5 steps changes in the next 5 seconds should be reasonable.
However this all needs careful control and you also need to think about how the transfer back to mains power is arranged. Automatic or manual? What happens if the power if restored while the loads are being switched on the the generator?
Sorry for the delayed answer.
Thank you for reminding me about these details.
I think that the simplest way is that the transfer back to mains to be made manually. I think some ATS have implemented this function - i found this text on a specification: "if the mains supply becomes available again before the generator circuit breaker has closed then the mains circuit breaker remains closed (or recloses if it has opened) and the generator will not go on load.".
Are all these details manageable by a PLC?