Fire Supports on Cat5 cables EICR

Former Community Member
Former Community Member
Hope im in the right section.


Doing an EICR, and the install has a false ceiling which is a drop out tile from the grid. Orginal install very good with Trunking and tube, all on hangers and fixed with anchors to the slab. So no problems there.

Then Mr IT guy, has lashed cat5 cables across the ceiling, just laying on the ceiling grid. So with 18th edition, and with cat5 being POE, as an inspector Im thinking about coding as a C3, as under collaspe, these cables would drop to floor. Or should I just leave alone as maybe not part of the electrical system?


Thanks
Parents
  • Part of the structure, innit.

    OK, that wasn't a well chosen example...


    My point was that compliance with a BS shouldn't be the only or even the main criteria for deciding whether something is suitable - especially for an EICR where we're meant to be deducing whether the installation is safe for continued use (using thee current version of the regs as a yardstick for the level of safety to be expected). Some things that don't have a BS (I'm now thinking of proprietary systems like unistrut) are likely to perfectly satisfactory in practice and their actual safety or suitability isn't really reduced at all by the lack of a bit of paper certifying compliance with something or other. Likewise just because and item of equipment does comply with a BS it doesn't necessarily mean it's suitable for every particular situation (the debacle with BS 1363 sockets and EV charge points come to mind).


    For sure compliance with a BS is a nice easy way of palming off most of the hard thinking onto someone else and of course BS 7671 demands a certain level of compliance for a new installation - but we should not overlook the judgement that should also be applied in every situation.


    Most ceiling grids for example are intended to directly supply 4'x2' light fittings - weighing in at several kg each - is it really plausible to suggest a few tens of grams of cat 5 in the same area will make an appreciable difference to the systems support capabilities?


    I do agree that slinging cables over a grid isn't exactly good practice - but sometimes there are few alternatives especially when the ceiling is already up and the space underneath a fully populated office. CAT 5 (and higher) really doesn't want to be supported from a catenary wire with a few ty-wraps (data cable installation standards demand protection of the cable's geometry for performance reasons) and getting anything like tray or basket up there is likely to be difficult and disruptive - i.e. expensive - and customers tend to prefer cheaper solutions.


       - Andy.
Reply
  • Part of the structure, innit.

    OK, that wasn't a well chosen example...


    My point was that compliance with a BS shouldn't be the only or even the main criteria for deciding whether something is suitable - especially for an EICR where we're meant to be deducing whether the installation is safe for continued use (using thee current version of the regs as a yardstick for the level of safety to be expected). Some things that don't have a BS (I'm now thinking of proprietary systems like unistrut) are likely to perfectly satisfactory in practice and their actual safety or suitability isn't really reduced at all by the lack of a bit of paper certifying compliance with something or other. Likewise just because and item of equipment does comply with a BS it doesn't necessarily mean it's suitable for every particular situation (the debacle with BS 1363 sockets and EV charge points come to mind).


    For sure compliance with a BS is a nice easy way of palming off most of the hard thinking onto someone else and of course BS 7671 demands a certain level of compliance for a new installation - but we should not overlook the judgement that should also be applied in every situation.


    Most ceiling grids for example are intended to directly supply 4'x2' light fittings - weighing in at several kg each - is it really plausible to suggest a few tens of grams of cat 5 in the same area will make an appreciable difference to the systems support capabilities?


    I do agree that slinging cables over a grid isn't exactly good practice - but sometimes there are few alternatives especially when the ceiling is already up and the space underneath a fully populated office. CAT 5 (and higher) really doesn't want to be supported from a catenary wire with a few ty-wraps (data cable installation standards demand protection of the cable's geometry for performance reasons) and getting anything like tray or basket up there is likely to be difficult and disruptive - i.e. expensive - and customers tend to prefer cheaper solutions.


       - Andy.