Cpc

Is it acceptable practice to crimp a cpc with through crimps to extend it?
Parents
  • MrJack96:

    Is it acceptable practice to crimp a cpc with through crimps to extend it? 


    526.3 "Every connection shall be accessible for inspection, testing and maintenance, except for the following:



    (iv) A joint made by welding, soldering, brazing or appropriate compression tool.

    …"


Reply
  • MrJack96:

    Is it acceptable practice to crimp a cpc with through crimps to extend it? 


    526.3 "Every connection shall be accessible for inspection, testing and maintenance, except for the following:



    (iv) A joint made by welding, soldering, brazing or appropriate compression tool.

    …"