UKPN:
Quite correctly, you choose not to use the PME supply, The ESQCR regulations make it clear that this kind of structure, with a steel covering needs an independent earth. The DNOs requirement is 2 meters separation from any metalwork connected to the PME network, which I am confident you can establish.
Regards, UKPN ?
The BS 7671 requirements for simultaneous contact between earthing systems is 2.5 m (arm's reach).
As I said earlier, the separation of earth electrodes to buried metalwork underground is a separate requirement.
UKPN:
Quite correctly, you choose not to use the PME supply, The ESQCR regulations make it clear that this kind of structure, with a steel covering needs an independent earth. The DNOs requirement is 2 meters separation from any metalwork connected to the PME network, which I am confident you can establish.
Regards, UKPN ?
The BS 7671 requirements for simultaneous contact between earthing systems is 2.5 m (arm's reach).
As I said earlier, the separation of earth electrodes to buried metalwork underground is a separate requirement.