UKPN:
Quite correctly, you choose not to use the PME supply, The ESQCR regulations make it clear that this kind of structure, with a steel covering needs an independent earth. The DNOs requirement is 2 meters separation from any metalwork connected to the PME network, which I am confident you can establish.
Regards, UKPN ?
The BS 7671 requirements for simultaneous contact between earthing systems is 2.5 m (arm's reach).
As I said earlier, the separation of earth electrodes to buried metalwork underground is a separate requirement.
Sparkingchip:
The correct answer is probably TT the entire installation.
Andy B.
The latest guidance for that which has been published in Annex H of the IET Code of Practice for Electric Vehicle Charging Equipment Installation, 4th Edition, is 10 m separation underground between buried metalwork and earth electrodes connected to the converted TT system, and buried metalwork and earth electrodes connected to the PME system.
AJ, just to be clear, what PME potential are you referring to, is it a heavily loaded neutral or a broken one?