lyledunn:
Andrew, apologies for butting in with a supplementary question. Is the so called leakage current a different concept to the protective conductor or touch current? In the COP for In-service Inspection and Testing of Electrical Equipment a maximum of 0.25mA is permitted or double that if the equipment has no control device or is fitted with a control device which provides 3mm clearance in the off position. That is in-service, I know, but it would seem to tally with what Graham said. However, I was under the impression that the protective conductor current was measured with a simulated body resistance of 1000ohms.
Isn't that "touch current" Lyle?
Protective conductor current in terms of BS 7671 is protective conductor current from whatever source (i.e. it's undefined) and therefore includes current collected from EMI absorbed by shielding, and "leakage currents" from interconnected equipment, as well as standing protective conductor currents from noise filters on the mains, and "leakage" across insulation and transformers.
Product standards may define protective conductor current measurements and/or touch current measurements - the touch current measurements being in the way you have defined (it's a combination resistive and capacitive network to simulate a dry body impedance).
lyledunn:
Andrew, apologies for butting in with a supplementary question. Is the so called leakage current a different concept to the protective conductor or touch current? In the COP for In-service Inspection and Testing of Electrical Equipment a maximum of 0.25mA is permitted or double that if the equipment has no control device or is fitted with a control device which provides 3mm clearance in the off position. That is in-service, I know, but it would seem to tally with what Graham said. However, I was under the impression that the protective conductor current was measured with a simulated body resistance of 1000ohms.
Isn't that "touch current" Lyle?
Protective conductor current in terms of BS 7671 is protective conductor current from whatever source (i.e. it's undefined) and therefore includes current collected from EMI absorbed by shielding, and "leakage currents" from interconnected equipment, as well as standing protective conductor currents from noise filters on the mains, and "leakage" across insulation and transformers.
Product standards may define protective conductor current measurements and/or touch current measurements - the touch current measurements being in the way you have defined (it's a combination resistive and capacitive network to simulate a dry body impedance).