electric showers

Former Community Member
Former Community Member
Hello again, following on from the recent topic that discussed sizing electrical supplies to fixed equipment we have been asked to install 4 number 9KW electric showers into the same commercial premises as my earlier question on RCD protection to lighting.

Designer has asked for a 250A SPN sub board, (3 phase supply is available) and 4 x 60A SPN supplies to the showers with 60A DP isolators. When I checked the model MI they state a 40A supply is required. I queried this with the designer and his answer is that the showers draw 39A so wants the 60A supplies. Apart from the fact I can't find a decorative DP switch rated at 60A, am I missing something in that this feels unnecessary. No cable sizes have been discussed yet, 

Showers are on an office floor with 200 or so desks so assuming similar numbers of staff although not convinced that all staff will be lining up to use the showers on a daily basis. 

Again thanks in advance for any thoughts.
Parents
  • It does sound somewhat oversized for four 40A loads. 

    If the intention is that the RCBOs or MCBs + RCDs are all side by side, then it is not unusual to ue a 50A device for a 40A load, to reduce problems with one breaker heating its neighbours and skewing the thermal trip threshold.  The better way to do this is not to put fully loaded breakers side by side, but to leave a gap or to  alternate with light loads.


    Is the intention to add additional loads in the future ? If not then a 80A 3 phases would cover it better, and still have capacity for 6 showers.
Reply
  • It does sound somewhat oversized for four 40A loads. 

    If the intention is that the RCBOs or MCBs + RCDs are all side by side, then it is not unusual to ue a 50A device for a 40A load, to reduce problems with one breaker heating its neighbours and skewing the thermal trip threshold.  The better way to do this is not to put fully loaded breakers side by side, but to leave a gap or to  alternate with light loads.


    Is the intention to add additional loads in the future ? If not then a 80A 3 phases would cover it better, and still have capacity for 6 showers.