Johno12345:
if we all think they will run fine all day at the incomer rating, then all should be ok, and I'm just over thinking things a bit
I think you said maximum load sustained was 200A through a 250A rated DB - that should be fine
250A sustained through a 250A rated board is a different proposition - it will get hot, and then it depends on the quality of manufacture - sadly, many DB's won't survive full load for extended periods
Regards
OMS
Johno12345:
if we all think they will run fine all day at the incomer rating, then all should be ok, and I'm just over thinking things a bit
I think you said maximum load sustained was 200A through a 250A rated DB - that should be fine
250A sustained through a 250A rated board is a different proposition - it will get hot, and then it depends on the quality of manufacture - sadly, many DB's won't survive full load for extended periods
Regards
OMS