This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Extraction fan in a bathroom

Former Community Member
Former Community Member
I have limited areas my fan can go. It is going to have be wall mount at the other end of my bath/shower head. My consumer unit is 30mA RCD protected. 


I have found a fan 

MONSOON ZONE 1 SILENCE TIMED EXTRACTOR FAN MON-S100T




it is main powered, I can’t do a 12v as there is No where the transformer can go.


is the monsoon okay to use? It says zone 1? 


Parents
  • 701.55 permits the use of ventilation equipment in zone 1 subject to being suitable according to the manufacturer's instructions. From the sound of it, it is in zone 2, or even outside the zones.


    Having the fan go on and off in parallel with the light, as opposed to running on for a period, probably contravenes building regulations.
Reply
  • 701.55 permits the use of ventilation equipment in zone 1 subject to being suitable according to the manufacturer's instructions. From the sound of it, it is in zone 2, or even outside the zones.


    Having the fan go on and off in parallel with the light, as opposed to running on for a period, probably contravenes building regulations.
Children
No Data