I have found a fan
MONSOON ZONE 1 SILENCE TIMED EXTRACTOR FAN MON-S100T
it is main powered, I can’t do a 12v as there is No where the transformer can go.
is the monsoon okay to use? It says zone 1?
geoffsd:
Of course, but previous posters claimed that The Building Regulations state that a bathroom fan must be fitted - and therefore must be legally compulsory.
Further, it was even claimed that The Building Regulations state that a timed run-on must be incorporated - and therefore must be legally compulsory.
Neither is true.
Statute requires "adequate ventilation". The approved document and other guidance such as The Electrician's Guide to the Building Regulations provide guidance as to what is adequate. Adequate ventilation includes purge ventilation which may be achieved by having at least one opening window of sufficient size, or a fan with a 15 minute overrun.
The work described in the OP may fall outside the scope of the Building Regulations, but in any applicable work, it would seem foolhardy not to provide a switched line and an un-switched line.
Incidentally, I am not convinced that a 3-pole isolator is necessary, but it is desirable.
geoffsd:
Of course, but previous posters claimed that The Building Regulations state that a bathroom fan must be fitted - and therefore must be legally compulsory.
Further, it was even claimed that The Building Regulations state that a timed run-on must be incorporated - and therefore must be legally compulsory.
Neither is true.
Statute requires "adequate ventilation". The approved document and other guidance such as The Electrician's Guide to the Building Regulations provide guidance as to what is adequate. Adequate ventilation includes purge ventilation which may be achieved by having at least one opening window of sufficient size, or a fan with a 15 minute overrun.
The work described in the OP may fall outside the scope of the Building Regulations, but in any applicable work, it would seem foolhardy not to provide a switched line and an un-switched line.
Incidentally, I am not convinced that a 3-pole isolator is necessary, but it is desirable.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site