Testing a building where the fire alarm in another building has been extended into the 1 I am testing. the old wiring has been used and is laid with a metal trunking.

Just wondered what that thought is on coding??
Parents
  • Agree. So long as the 24v cable insulation matches that of the cables carrying the highest voltage present in the trunking then all should be ok.
Reply
  • Agree. So long as the 24v cable insulation matches that of the cables carrying the highest voltage present in the trunking then all should be ok.