John Peckham:
Chris
I assume that you are being provocative to stimulate debate? Whilst I am pleased to hear that you and Mrs P have previously returned from a holiday in France safely that cannot be the basis for substituting this experience for the requirements of BS 7671!
Pot calling kettle ... pot calling kettle ...
Well now, what code would others have given?
I mention France only 'cos the last two hotels in which we stayed had sockets in the bathrooms - by the wash hand basins rather than the bath.
John Peckham:
Wally
Can I assume you do not have a complete set of those qualifications?
I'm not sure what your point is. I don't currently do EICRs and have no intention to start. That doesn't affect whether my comments on the current legal situation are true or not.
I am sympathetic to the view which states that if the installation fully complied with regulations at the time, and still do - that is, it is in good condition - then I would deem it to be safe for continued use despite the lack of the fulfillment of any of today's requirements.
1.Using a public utility water pipe as a means of earthing? Compliant in 13th Edition.
2. No RCD protection for a 230V socket that could supply portable equipment outside? Compliant 14th Edition.
3. A bedroom with a show cubical with a 230V socket 2.5m from the shower? Compliant with the 15th edition.
4. A surface run wiring system on a ceiling without metalic support? Compliant with the 16th Edition.
5. An electric vehicle charging point connected to a PME earthing system without one of the special provisions for neutral. Compliant with 17th Edition.
John Peckham:
Andy
Your item 4. Why a C2 only for an "escape route" . You might want to have a look what it says on Page 5 of the 18th Edition. 2 of the fire fighters killed were killed by entanglement in a bedroom. Also have a look at the BS 7671 definition in Part 2 of an "Escape Route". I like my ex senior fire officer, now fire risk assessor, definition myself, "laying on your bed or chopping tomatoes in your kitchen to the final exit door from the premises".
If I may butt in ...
I was hinting at that definition of an escape route in my posting. If my workshop is on fire and I'm still in it, I will have been overcome by smoke; or I have blown something up with me alongside it. I don't see how the cables on the ceiling could entangle anybody. In a sense, I don't think that they could collapse prematurely, because the term in that context is meaningless.
Bear in mind that most private houses don't have escape routes, but if I'm asleep and the fire alarm goes off, it is vital that any surface mounted cables on the ceiling between me and an outside door don't collapse until I am out of the building. Now the term "prematurely" has meaning.
Any road, at least now we have a range of opinion. ?
Your item 4. Why a C2 only for an "escape route"