Alasdair Anderson:
Sounds to me as if there could be capacitance in the circuit. The reading rises as the capacitance charges up until it reaches a stable reading when the capacitance is fully charged. This is most often seen on very long cable runs due to the cable capacitance.
Sparkingchip:
For testing a domestic socket circuit they are both more than adequate, as the minimum requirement according to the wiring regs is 1 Mohm and that is not set in stone, the HSE recommend 2 Mohm, but it may be considered that less than 1 Mohm is acceptable depending on the circumstances.
Andy Betteridge
The minimum requirement in 7671 is set for new installations and is required to be 1Mohm minimum when the test is applied to the distribution circuit with all the final circuits on but connected equipment removed. Thus two final circuits at 1Mohm would mean failure. For periodic inspections, there used to be a recommendation in GN3 that a final circuit should not fall below 2Mohms. That was removed for further editions but I note that in the most recent version there is reference to using the 1Mohm merely as a reference for taking a view.
mike would maybe know how these IR testers work but I think that the applied voltage is increased incrementally.
edit to ask Andy for the HSE reference for the 2Mohms.