10kw 3 Phase A/C what type of protection is required?
Another query from a non-electrician, hoping to get some guidance from the experts on how to handle my air conditioner install.
So I am in a predicament where I have a 3 phase distribution box (PME, 100A, 400V phase to phase supply) that is fully populated by RCBO's and hence has no RCD of it's own so unsure of what protection to use at the main distribution box (DB).
Is it okay to use just a 3 pole MCB of the correct rating (20A) to protect the circuit supplying power till the isolator? Since there is no 4 pole RCBO from Hager unsure what I need to do for earth fault protection (if required).
Apparently 18th edition mandates RCD protection for all circuits? Appreciate your insights please.
Looking for options where I do not have to install a seperate consumer unit and all the protection can be done from the existing DB. Appreciate your help!
More details on the installation below,
  • DB - Hager Invicta 3 range
  • Mitsubishi Heavy Industries - 3 phase outdoor unit - 10kw (power supply from DB)
  • Mitsubishi Heavy Industries - Single phase indoor unit - (power supply from outdoor unit)
  • Power to outdoor unit: We have used 4mm 5 core SWA from the DB to a 4 pole IP65 isolator on the outside of the property (cable sheath is earthed using a earth cable crimped to the earth bar of the DB (same earth slot for the Aircon power supply).
  • Power to indoor unit: The compressor (outdoor unit) then uses SY cable to supply power and communicate with the indoor unit. I have used PVC table to protect the SY cable since it is not outdoor rated and put the cable inside plastic trunking so there is no exposed SY cable.
  • Presumably the RCBOs are all single phase with  neutral tail. If you need RCD protection for a load with a neutral connection, you will need a 4 pole sensing device and that will not fit a 1,2,3 bus bar.
  • I am not sure why you need additional protection for this device - no sockets involved!
    As an aside, other manufacturers (e.g. Eaton, Schneider) do make 4-pole RCBOs; Eaton's occupy 4 x 18 mm ways.
    Chris Pearson:
    My NICEIC electrician suggested that it is required to have RCD protection since the AC has an outdoor unit that sits on a concrete slab slightly above soil level (he didn't use these exact words but suggested RCD protection is required for all circuits under 18th edition?).
    Can someone give me a reference to the regulation that shows RCD protection would not be required?
    Is there an exception for fixed installations that shows an MCB might be sufficient?
    Hager apparently do this Add on block but holy moley is it expensive, want to avoid unless required - BD163T - https://hager.com/uk/products/h/bd163t-add-on-block-3p-63a-30ma-a-1mod-el
    mapj1:
    Not sure this is entirely correct, apologies if I have misunderstood your comment.
    As per my other comment post on this there seems to be devices out there that can take up an empty space and still work?
  • FaeLLe:
    BS 7671 generally states what is required rather than what is not required. See 411.3.3 for sockets and mobile equipment for use outdoors.
    IIRC, the list price for Eaton's TPN RCBOs is about £500.
    Thanks for the information, this 3 phase A/C unit has been an expensive headache.... it better be worth the premium.
    Any thoughts (slightly off topic) if a 3 phase A/C will probably be more reliable (and cheaper?) in the long run as compared to a Single phase unit of similar capacity.
    You might need to look at MIs as Daikin for instance asks for a 300mA Type B RCD for their VRF condenser units, single or 3 phase.
  • FaeLLe:
    mapj1:
    I may have the wrong picture. you said the board is full of RCBOs - I was trying to ask how the neutral to them is organised.
    Also most 3 phase bus bar, and I am not familiar with this one, have tags that go L1 L2 L3 L1 L2 L3 , not
    L1 L2 L3  N L1 L2 L3  N. A repeat pattern of 4, rather than 3.
    An RCD or RCBO for a load with a neutral connetion, err, needs a neutral connection. 4 pole bus bar does exist but is not common.
    The bus bar line up  is all I was asking about. It is sometimes seen that the end tag of the bus bar is removed to allow a flying N tail, but it is not really a nice fix and needs to be done carefully and well insulated, or ideally avoided.
    mapj1:
    FaeLLe:
    mapj1:
    The Hager Invicta 3 has a seperate neutral and earth bar that lets you have a Neutral for each circuit (including a single phase circuit); so you can have a seperate N from the Neutral bar for each L1, L2, L3.
    Plus Hager is all Made in France including the RCBO's, big fan of them !
  • mapj1:
    The Memshield arrangement is L1 L2 L3 N (covering L1) L2 L3 L1, etc. AFAIK, there is no reason why you should not put 3 of these RCBOs on each side of an 8 way board. Alternatively, you fill the gaps with SP devices or blanks.