Cross sectional area of a protective conductors

Can someone give me a some advice on if we have a earth electrode system made up of the structural rebar when using the adiabatic equation to size of the bonding conductor comes out at 300mm. MY questions is does each bond need to be this size or can it be made up via a series of smaller bonds that are equal or exceed the 300mm requirement? My opinion is each bond needs to be this size to deal with the fault current as the direction it will flow is unknown. What are peoples thoughts? I cannot see anything in the regs on this.

  • What is the voltage and current of the system, and what is the electrode resistance to terra- firma.?


    Unless this is part of a lightning system or perhaps an indoor substation,  I'd be surprised if any electrode on an LV system, could really sink enough current to need a 300mm bond during the time needed to clear a fault, and 'd have no issue with doing that  with a small no. of more conveneint sized cables.

    What is the cross section of the re-bar that you are connecting to ? After all there is no point in connecting 300mm sq of copper to 500mm2 of steel ?
  • Former Community Member
    0 Former Community Member
    The adiabatic expression wouldn't size the bonding conductor - only the main earthing conductor, from which you can derive the bonding conductor size depending on the earthing arrangements.


    300mm2 seems a fantastically large conductor to be using for bonding. It might be credible for earthing but would be unusual. As an example, it's perfectly feasible to operate a pair of 1.5MVA transformers with a combination of a single 95mm2 conductor and the transformer tails armouring. Assuming this is a fairly large installation, and if you really do need a 300mm2 conductor, then personally speaking, I would use two conductors if you have the opportunity to split up the electrode for testing in future - other than that, I would favour a single conductor  - although there is no reason not to use more, smaller conductors as long as you are assured they all stay in place


    Regards


    OMS
  • The fault current for the project is abnormally large exceeding 90kA hence the protective bonding conductor size, note the earthing is part of a global earthing system.  

    400V / 5MVA supply. The impedance of the electrode system is 1.369 ohms

  • Well 1.39 ohms, (by the way, a surprisingly precise number,  is that a test result or calculation ?) will pass less than 200A  into earth, assuming we are talking about the bit of cable that only goes to the electrode. As such, even if the fault was never cleared, in practice a piece of 50 or 70 mmsq would probably do. The stuff that does carry the full fault current is going from the supply neutral to the CPC that goes to the enclosures for the live parts. I presume the 90kA fault current does not go very far before the impedance of the cables themselves reduce the prospective fault current quite a bit.
  • MS01:
    The fault current for the project is abnormally large exceeding 90kA hence the protective bonding conductor size, note the earthing is part of a global earthing system.  

    400V / 5MVA supply. The impedance of the electrode system is 1.369 ohms

     


    If it's a normal 400/230V system (so 230V to Earth) and the electrode has a resistance of 1.369 Ω then, by Ohm's Law, I don't see how more than 168A can flow through the conductors to your electrodes.


    OK it might be wise to leave a generous margin in case the electrodes have a lower resistance after some wet weather, but even so a 4mm² might be adequate.


       - Andy.


  • Former Community Member
    0 Former Community Member
    Can you describe, in a bit more detail, or show a sketch of, the conductor you are talking about because there is something adrift with the numbers being quoted.


    If it's the connection from the switchboard back to the transformer star point then this is usually the "neutral" conductor - everything else is G/Y and is probably either equipotential bonding, or the connection to the neutral to create the reference - so even in a 5MVA installation probably isn't bigger than a range between (say) 50mm2 and 95mm2


    Regards


    OMS
  • A bit more detail it’s a new build development with a 5MVA supply (2x2.5MVA TX's) so the fault level by tweaking the impedance is just below 100kA. The site is cold but as its HV metered soil resistivity test have been carried and structural rebar and a number of piles. The rebar is in line with BS50522 and is 50mm² and incased in concrete. From the Rebar there are a number of bonds to earthing bars around the development.

    Now the fault level used by the earthing specialist is 1.77kA given by the DNO, however my concern is a fault on the LV side where the fault current could be as high as 100kA.  

    EPR etc isn’t an issue as its global earthing system, but the question is should the bonds to the rebar be cable of taking the high fault current?
  • MS01 - I'm sure you are confusing potential fault current PFC (Live to Live or Live to Neutral) with potential earth fault current PEFC (Live to earth). 


    I'm no engineer so I hesitate to comment (Let alone with an installation of this size) but the I understand that the impedance of the Live to Neutral fault path  give you an approximation of the PFC - and if you multiply this by root 3 you'll get an approximation of the live to live fault current.


    The live to earth (PEFC) size depends on the live to earth impedance. As shown above by AJ - this'll only be 168 Amps......And that'll be your main earth fault path I believe. 


    When you say you have an earth electrode system made up of structural rebar - is this what needs bonding?


    I must be missing something.........


    If you look at Table 54.8 in the regs book - page 203 - this would indicate that your main bonding size should be circa 50mm if its PME or if you look at 544.1.1 - 25mm if TNS. It doesn't seem to have any limitations on this size.....


  • Former Community Member
    0 Former Community Member
    I think you need to draw the line diagram, and then look for those parts of the installation that carry earth fault current.


    Typically, both your transformers are closed into the switchboard and would have to be in parallel to achieve the fault level you quote. Presuming you can identify the N-E bond as either at the transformer, or more credibly at the switchboard, you should see that by far the largest proportion of fault current will return along that conductor in an earth fault.


    That conductor is referenced to earth via connections to the electrode - the resistance of which sets how much fault current can flow from bonding to rebar and back to the source point.


    Assuming all of your cabling design is "normal" and has adequately sized CPC's, then the bonding cannot see a fault current of 100/1.73 kA


    Regards


    OMS
  • Still feels a bit odd - if the 1.7kA is the HV side to earth fault current, we are looking at  6.4kV to ground (for 11kV phase to phase) so perhaps the HV electrode impedance is  something like 3.8 ohms

    Well perhaps not really, that is HV electrode plus the HV phase loop impedance, but  at  5MW  you are looking at perhaps 150 amps per line  on the primary at full load I'd assume the HV feed is not drooping by 10%  at that point -or there will be horrible problems of secondary side voltage drop)

    Presumably then most of the HV fault loop is indeed electrode related and it is at least a couple of ohms. and may be more like 3. Part of me is then a bit surprised that HV and LV earths are combined - it does not sound a very 'cold' site (due to LV side bounce during HV faults).


    In any case, you will not get thousands of amps flowing into your rebar, which is as well, as the rebar would probably need to be beefed up to take it, so the cable to the rebar can be reduced accordingly.