MS01:
The fault current for the project is abnormally large exceeding 90kA hence the protective bonding conductor size, note the earthing is part of a global earthing system.
400V / 5MVA supply. The impedance of the electrode system is 1.369 ohms
If it's a normal 400/230V system (so 230V to Earth) and the electrode has a resistance of 1.369 Ω then, by Ohm's Law, I don't see how more than 168A can flow through the conductors to your electrodes.
OK it might be wise to leave a generous margin in case the electrodes have a lower resistance after some wet weather, but even so a 4mm² might be adequate.
- Andy.