Tripping unit

4ea88f7627b6a3a0242311122cfae631-huge-ef2d9fec-e55a-4f9b-b6d3-12f6caced9f2.jpg
Parents
  • Hmm this is a brand new and slightly undersized installation.

    It also looks from the pic as if the overload is not equal on all 3 phases. Is the meter showing the hottest phase ? a pair of 120mm tri-rated tails is not quite enough for 1kA, you may manage better with 2 lots of 185 or even  240mm2  depending if the load is sharing equally, and how good is airflow. ( some typical rating data)- though the fact they look more cooked near the termination is telling.  I also wonder how sound the crimping is


Reply
  • Hmm this is a brand new and slightly undersized installation.

    It also looks from the pic as if the overload is not equal on all 3 phases. Is the meter showing the hottest phase ? a pair of 120mm tri-rated tails is not quite enough for 1kA, you may manage better with 2 lots of 185 or even  240mm2  depending if the load is sharing equally, and how good is airflow. ( some typical rating data)- though the fact they look more cooked near the termination is telling.  I also wonder how sound the crimping is