OMS:
As a quick sanity check, and using 240V, we know 1kw is 4A at 240V
Regards
OMS
Hi OMS, Has your account been hacked? 1 kW is 4A at 250 V?
weirdbeard:OMS:
As a quick sanity check, and using 240V, we know 1kw is 4A at 240V
Regards
OMSHi OMS, Has your account been hacked? 1 kW is 4A at 250 V?
True - but we tend not to talk about the single phase voltage being 250, we usually say it's 240V when discussing single phase
Much the same as we tend to say "ohh, that's a 415Volt Dist Boad"
None are strictly correct, just that it's an Old Skool way, to rapidly sanity check something where the engineer is focusing on the third decimal place and perhaps not seeing the big picture
For the OP, it would be enough to suggest you need a 400A TP&N service, providing 300kVA - which may just suggest for a particular project, that more diversity may need to be applied - particularly in comparison to other similar facilities
Best Regards
OMS