16A on Ring

Evening all,


I have a client who is looking for their swimming pool heat pump to be wired up. Manual requests for a 16A connection (although client has been running off a 13a plug!!).

The layout of the house and garden restricts the direct connection to the CU to being long and messy. 


The most direct route is to the lower socket ring. Im sure I remember reading on the old forum that a 16a RCD can be classed as a FCU. 

I can not seem to find reference to this in the regs though, is it stated in there?


If it is acceptable I could spur off this lower ring, in to a weatherproof CU with a double pole 16A RCD, then run SWA up the garden to the heat pump. 


Cheers

Rusty

Parents
  • it might be possible to split the "lower socket ring" into two lower rated radial circuits, and create a dedicated supply to the heat pump by making the break at the nearest socket outlet to the CU on one leg of the original ring. Although I agree with all the above replies, need serious thought and both new circuits would be notifiable.
Reply
  • it might be possible to split the "lower socket ring" into two lower rated radial circuits, and create a dedicated supply to the heat pump by making the break at the nearest socket outlet to the CU on one leg of the original ring. Although I agree with all the above replies, need serious thought and both new circuits would be notifiable.