16A on Ring

Evening all,


I have a client who is looking for their swimming pool heat pump to be wired up. Manual requests for a 16A connection (although client has been running off a 13a plug!!).

The layout of the house and garden restricts the direct connection to the CU to being long and messy. 


The most direct route is to the lower socket ring. Im sure I remember reading on the old forum that a 16a RCD can be classed as a FCU. 

I can not seem to find reference to this in the regs though, is it stated in there?


If it is acceptable I could spur off this lower ring, in to a weatherproof CU with a double pole 16A RCD, then run SWA up the garden to the heat pump. 


Cheers

Rusty

Parents
  • Sparkingchip:

    I have assumed the original poster is the same RustyH as on the old forum.


    We had a Discussion  started by RustH four years ago about matters relating to socket ring circuits, it didn’t actually go into the issues of supplying ornamental pond equipment, which this one already is or supplying swimming pool equipment as is proposed.


    A discussion forum is not the place to redesign this socket circuit, it needs someone onsite to decide what needs to be done. Raising questions about technical issues on a forum is one thing, trying to do the complete design is another.


     Andy Betteridge 




    Hi Andy,


    Correct, I used to use the old forum during my training and had some fantastic help from a number of members that are still active on this forum, which is great to see. 


    The questions back then where indeed regarding ring circuits, questions I had during my training. 


    This question was merely to seek some guidance on what I had read on this forum previously to do with adding a 16A RCD / MCB on a ring.


    Surely a forum is a place to allow those who may not have gained years and years of experience yet to ask questions they have uncertainty of, and get guidance from those that may have been in that situation before. 

    It also allows those questions to be in the domain for others that might be unsure at the time of assessing a job to research the answers on the forum. 


    I don’t feel I have asked for anyone to design me the circuit, I have thrown up what I think would be right and guidance has been shared. 


    If you feel the questions I have asked are not to the protocol the forum is trying to promote that please could you get a member of the admin team contact me to advise what is acceptable and not acceptable in this forum. 


    Much appreciated 

     


Reply
  • Sparkingchip:

    I have assumed the original poster is the same RustyH as on the old forum.


    We had a Discussion  started by RustH four years ago about matters relating to socket ring circuits, it didn’t actually go into the issues of supplying ornamental pond equipment, which this one already is or supplying swimming pool equipment as is proposed.


    A discussion forum is not the place to redesign this socket circuit, it needs someone onsite to decide what needs to be done. Raising questions about technical issues on a forum is one thing, trying to do the complete design is another.


     Andy Betteridge 




    Hi Andy,


    Correct, I used to use the old forum during my training and had some fantastic help from a number of members that are still active on this forum, which is great to see. 


    The questions back then where indeed regarding ring circuits, questions I had during my training. 


    This question was merely to seek some guidance on what I had read on this forum previously to do with adding a 16A RCD / MCB on a ring.


    Surely a forum is a place to allow those who may not have gained years and years of experience yet to ask questions they have uncertainty of, and get guidance from those that may have been in that situation before. 

    It also allows those questions to be in the domain for others that might be unsure at the time of assessing a job to research the answers on the forum. 


    I don’t feel I have asked for anyone to design me the circuit, I have thrown up what I think would be right and guidance has been shared. 


    If you feel the questions I have asked are not to the protocol the forum is trying to promote that please could you get a member of the admin team contact me to advise what is acceptable and not acceptable in this forum. 


    Much appreciated 

     