Motor overload

What would make an motor overload trip before a breaker when a motor is to earth?
Parents
  • It was a 3 phase motor. Top bearing had gone and it was tripping the overload in a few seconds of running. When doing an IR test on the motor it was to earth. The resistance to earth was 1.8ohms.
Reply
  • It was a 3 phase motor. Top bearing had gone and it was tripping the overload in a few seconds of running. When doing an IR test on the motor it was to earth. The resistance to earth was 1.8ohms.