AJJewsbury:
Similarly there are margins built into overcurrent protective devices - e.g. an MCB shouldn't trip when carrying current 13% above its rating (at least not for conventional time - usually an hour), Likewise cables would be expected to carry those sorts of currents above their ratings for such periods without significant damage (otherwise our whole approach to overload protection - In ≤ Iz falls apart). So it would be logical for the same to apply to accessories such as plugs and sockets (unless their product standards say otherwise).
On that basis, we would ignore BS1363 and go by the characteristics of BS1362 fuses. If it doesn't blow the fuse, it must be safe! ?
Incidentally, I have (moulded on) 13 A plugs which are rated at 3 A or 5 A.
AJJewsbury:
Similarly there are margins built into overcurrent protective devices - e.g. an MCB shouldn't trip when carrying current 13% above its rating (at least not for conventional time - usually an hour), Likewise cables would be expected to carry those sorts of currents above their ratings for such periods without significant damage (otherwise our whole approach to overload protection - In ≤ Iz falls apart). So it would be logical for the same to apply to accessories such as plugs and sockets (unless their product standards say otherwise).
On that basis, we would ignore BS1363 and go by the characteristics of BS1362 fuses. If it doesn't blow the fuse, it must be safe! ?
Incidentally, I have (moulded on) 13 A plugs which are rated at 3 A or 5 A.