Maximum sustained current perrmitted from 13 amp plug ?

This sounds an overly simplistic question, and the obvious answer is of course 13 amps. There is a clue in the name you know.


However in the case of a simple resistive load, the current will increase at a higher supply voltage. So at what voltage is the current measured for approval purposes ?

At 230 volts, the nominal or declared voltage ?

At 240 volts, the average voltage actually supplied most of the time in most places ?

Or at 253 volts, the maximum permitted. Or even at 256 volts the maximum achieved in an outbuilding with a bit of voltage rise due to grid tied PV on the roof.


The question has arisen due to a number of brand new "fast boiling" domestic electric kettles of reputable make failing a third party  PAT test due to "excessive current"


I repeated the test with my PAT tester and achieved a similar result, FAIL  in the premises in which they are to be used, but "pass" if tested elsewhere.

Tests with a variac and calibrated ammeter showed that a cold kettle on a 250 volt supply uses nearly 14 amps. just under 13 amps at 230 volts, both figures declining a little as the water starts to heat.

Had I done the original testing, I would have been inclined to use a little common sense and discretion and to pass an appliance that uses less than 10% overcurrent for a few minutes.

I would not pass an appliance such as a space heater that used even a slight overcurrent for hours at a time.


Wondered what others think.


And whilst we are on the subject, what about large portable air conditioners ? Available to hire fitted with 13 amp plugs, they appear to be a constant wattage load and use nearly 15 amps if the supply voltage is very low, and almost exactly 13 amps at 240 volts.
Parents
  • Some interesting points made, thanks for the replies.

    Had I tested the new kettles I would have  been inclined to pass them in view of the very short term use.


    I can not however agree with those who state that a space heater drawing 14 amps is OK. I have seen far too many 13 amp plugs that have failed under very modest overload, or even long term full load. Under modest overload the plug or the socket will often fail before the fuse operates.


    It would appear that most appliance manufacturers take a similar view, as most new appliances are limited to about 10 amps, possibly due to warranty claims or adverse publicity about melted plugs.

    3Kw heaters are now hard to find as are 3Kw tumble dryers.
Reply
  • Some interesting points made, thanks for the replies.

    Had I tested the new kettles I would have  been inclined to pass them in view of the very short term use.


    I can not however agree with those who state that a space heater drawing 14 amps is OK. I have seen far too many 13 amp plugs that have failed under very modest overload, or even long term full load. Under modest overload the plug or the socket will often fail before the fuse operates.


    It would appear that most appliance manufacturers take a similar view, as most new appliances are limited to about 10 amps, possibly due to warranty claims or adverse publicity about melted plugs.

    3Kw heaters are now hard to find as are 3Kw tumble dryers.