Maximum sustained current perrmitted from 13 amp plug ?

This sounds an overly simplistic question, and the obvious answer is of course 13 amps. There is a clue in the name you know.


However in the case of a simple resistive load, the current will increase at a higher supply voltage. So at what voltage is the current measured for approval purposes ?

At 230 volts, the nominal or declared voltage ?

At 240 volts, the average voltage actually supplied most of the time in most places ?

Or at 253 volts, the maximum permitted. Or even at 256 volts the maximum achieved in an outbuilding with a bit of voltage rise due to grid tied PV on the roof.


The question has arisen due to a number of brand new "fast boiling" domestic electric kettles of reputable make failing a third party  PAT test due to "excessive current"


I repeated the test with my PAT tester and achieved a similar result, FAIL  in the premises in which they are to be used, but "pass" if tested elsewhere.

Tests with a variac and calibrated ammeter showed that a cold kettle on a 250 volt supply uses nearly 14 amps. just under 13 amps at 230 volts, both figures declining a little as the water starts to heat.

Had I done the original testing, I would have been inclined to use a little common sense and discretion and to pass an appliance that uses less than 10% overcurrent for a few minutes.

I would not pass an appliance such as a space heater that used even a slight overcurrent for hours at a time.


Wondered what others think.


And whilst we are on the subject, what about large portable air conditioners ? Available to hire fitted with 13 amp plugs, they appear to be a constant wattage load and use nearly 15 amps if the supply voltage is very low, and almost exactly 13 amps at 240 volts.
Parents
  • I will answer another point Broadgauge, the appliance maximum power is less than it used to be because EU regulations are attempting "power saving" again. As for testers failing at 13A, what do they do with a 5W LED lamp? Do they still take 13A to issue a fail or do they know what was plugged in? Perhaps the 13A is because the tester cannot be CE marked if it has a 13A plug? Clearly another fools paradise.
Reply
  • I will answer another point Broadgauge, the appliance maximum power is less than it used to be because EU regulations are attempting "power saving" again. As for testers failing at 13A, what do they do with a 5W LED lamp? Do they still take 13A to issue a fail or do they know what was plugged in? Perhaps the 13A is because the tester cannot be CE marked if it has a 13A plug? Clearly another fools paradise.